Recently called out to a chalet that had problem with intermittent mcb tripping on the socket circuit ,putting that to one side just now ,The other fault I have not come across is the following ,Two outside lights switched together from 1x one way switch inside the chalet,Turn switch on nothing happens go to consumer unit switch off mcb that is intermittently tripping on socket circuit and two outside light come on and switch on and off using one way switch inside chalet ,”If anybody has come across a similar fault it would forever be appreciated “HELP”
 
Recently called out to a chalet that had problem with intermittent mcb tripping on the socket circuit ,putting that to one side just now ,The other fault I have not come across is the following ,Two outside lights switched together from 1x one way switch inside the chalet,Turn switch on nothing happens go to consumer unit switch off mcb that is intermittently tripping on socket circuit and two outside light come on and switch on and off using one way switch inside chalet ,”If anybody has come across a similar fault it would forever be appreciated “HELP”
Have you checked that there is a supply to the switch/light when it's failing?
Is there a sensor on the lights ?

Some mcbs after a trip need to be reset before they will switch.
 
Upvote 0
Have you checked that there is a supply to the switch/light when it's failing?
Is there a sensor on the lights ?

Some mcbs after a trip need to be reset before they will switch.
No supply to switch/light when not working ,no sensor ,and reset not required after mcb trips,What is really confusing is the fact that the lights do not switch on until the breaker that protects the socket circuit trips off,I’ve been a sparky for a long time and I have never came across this fault before. So please teach this old dog a new trick
 
Upvote 0
No supply to switch/light when not working ,no sensor ,and reset not required after mcb trips,What is really confusing is the fact that the lights do not switch on until the breaker that protects the socket circuit trips off,I’ve been a sparky for a long time and I have never came across this fault before. So please teach this old dog a new trick
Are the outside lights on the socket circuit ?
 
Upvote 0
Are the outside lights on the socket circuit ?
I can not say for definite yes or no as I have only had one visit to chalet to try and fix the original fault ie intermittent tripping of the socket circuit,and only came across the problem with lights during first visit ,so I left to go back after trying to find more information regarding lights,
 
Upvote 0
I can not say for definite yes or no as I have only had one visit to chalet to try and fix the original fault ie intermittent tripping of the socket circuit,and only came across the problem with lights during first visit ,so I left to go back after trying to find more information regarding lights,
N to earth fault or borrowed neutral ?

MCB off, the live wire is disconnected, but the earth wire still has an active connection back to the consumer unit. Because the neutral is now connected to earth, current can flow back through this unintended pathway, causing the lights to function.

MCB on, the L is reconnected, and the earth wire suddenly has a live current flowing through it.

I think a bit of testing is going to be needed.

No Rcd ?
 
Upvote 0
N to earth fault or borrowed neutral ?

MCB off, the live wire is disconnected, but the earth wire still has an active connection back to the consumer unit. Because the neutral is now connected to earth, current can flow back through this unintended pathway, causing the lights to function.

MCB on, the L is reconnected, and the earth wire suddenly has a live current flowing through it.

I think a bit of testing is going to be needed.

No Rcd ?
 
Upvote 0
No rcd is correct ,I did make a visual inspection of one way switch that controls two outside lights and your suggestion of a borrowed neutral seems a very high probability and a neutral to earth fault also incorporated in this scenario,,
I’m going back on Tuesday so I’ll let you know the outcome,But all I can say is Brilliant I think you have cracked it mate well done and many thanks
 
Upvote 0