netblindpaul
I'm confused by your last post DW

I'm confused by your last post DW

Why? A standard VFD for an Induction motor will ramp up both Frequency and voltage so as to limit inrush currents there are other drives and methods but your basic off the shelf model will ramp voltage up to full which will then be at plated base speed in line with frequency ...if you were to extend the ramp up from instant to slow say 10seconds and put you meter across the phases you will see the voltage rise to full over the 10seconds not full voltage straight away with frequency rise over the ramp but both together.
Because that was not the post I was confused by!
You blighter you've changed it!

Reading through this, not by any chance the motors are wired in delta whilst the inverters are set up for star connection? The output voltage is then too high. This you can't measure easily as the output is not a pure sine, too many harmonics are on it. Don't measure to earth, you will get rubbish. Just a thought...
If your getting a steady 300v and the meter isn't a cheap and nasty then the motor is probably not running at full speed if the users have a habit of running the motors at a slow speed the air passing over them may not be enough to cool the motor down with a standard induction motor where the fan on the opposite end is used to cool the motor while running everything is fine at base speed but if you run same motor at 25% of base speed then the fan also runs at 25% speed and won't be able to cool motor and the motor can burn out without been detected by drive until it fails.... in such cases where slow speed are required for long durations the a forced fed fan needs fitting that cools at full speed regardless of motor speed. As there are so many applications and set-up as well as different motors you need some background as i said before to know when things are an issue or whether its not a concern.That makes sence (and thanks for the graph) But the voltages that were measured were fairly stable.
Update 2:
Just went to test a few good units.
Tested one unit that had a different inverter inside (SSO 650) using my Metrel mx26 i got a nice steady 430v between phases.
I then found a unit with the same inverter as the u/s unit and measured between phases again.
On start up the voltage climbed steadily over a period of about 5 seconds.
It started at around 100v and finished holding steady at 379v.
Now the motors operating voltages are between 380-440v so this is obviously a little low (assuming my meter is being truthful)
So with this information can I assume that either these inverters are just not up to the job or that they have been programmed wrong?
Thanks for the continued advice btw.
Think ive learnt more about inverters in the last 24 hours than i ever have lol