Well you were right darkwood this thing is opening up more questions than closing off answers!!
So heres the update:
Went up to check voltage bands of the motors.
Delta: 380-420
Star: 660-720
So anyways curiosity got the better of me and I decided to check the wiring of each motors terminal blocks.
So first units motors were both wired in delta the same as the one motor I had checked before.
2nd unit first in delta (one i checked yesterday) and the second in Star!!
This is obviously a problem!
3rd unit both wired in star.
So now I am left with several questions the top of my list being who and why!!
Moral of the story and personal lesson for me:
Never assume things have been done properly!
So heres the update:
Went up to check voltage bands of the motors.
Delta: 380-420
Star: 660-720
So anyways curiosity got the better of me and I decided to check the wiring of each motors terminal blocks.
So first units motors were both wired in delta the same as the one motor I had checked before.
2nd unit first in delta (one i checked yesterday) and the second in Star!!
This is obviously a problem!
3rd unit both wired in star.
So now I am left with several questions the top of my list being who and why!!
Moral of the story and personal lesson for me:
Never assume things have been done properly!