Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok, when I did IR live and neutral to cpc I got 0Mohms, when I did resistance test got a very low reading 0. something.

Now I knew that there was something going on cause the rcbo was fine and it turned on which it would not if it was effectively a dead short.

So my theory and I just wanted to check this with others to make sure I am correct, supply is TNCS, 3 phase, passes through a 3 pole mcb to a distribution board that has only 3 pole isolator, rcbo will most likely have been single pole only, so my thinking is neutral is not isolated at all even when you turn off the rcbo and there is a path right back to the supply fuse where obviously earth and neutral become one. So doing Neutral to cpc I got a lot resistance reading and because loads were plugged in also got a low reading from live to cpc...

Because of this ended up putting it as a limitation, but is my theory correct? Obviously if I had disconnected the rcbo at the board then I could have done IR testing however the board was a bit of a mess and with it being live and not the easiest place to work on I thought it safer to do from a socket but obviously found the limitation that I could do end to end and R1+R2 but could not do IR. I guess this is also true of a board that has been isolated live and neutral the IR test will effectively be a global IR unless you disconnect the neutral. (Obviously IR was done at 250v and the megger does not actually let you ramp up anyway if reading is low.)
 
I guess this is also true of a board that has been isolated live and neutral the IR test will effectively be a global IR unless you disconnect the neutral
Yes, and forgetting a board had SP devices is exactly how I finished off a faulty fridge freezer once....
As you say you are effectively doing a L-E test of the circuit, and a N-E test of all circuits.

In your scenario I'd have looked to see if I could safely get the RCBO N fly lead out or the N conductors out of the RCBO.
EDIT being 101% sure I had the right one as I have no ambitions to become a N conductor.
 
Last edited:
Yes, and forgetting a board had SP devices is exactly how I finished off a faulty fridge freezer once....
As you say you are effectively doing a L-E test of the circuit, and a N-E test of all circuits.

In your scenario I'd have looked to see if I could safely get the RCBO N fly lead out or the N conductors out of the RCBO.

Yeah it was at the top of the board in a small cupboard and was a bit of a mess of cables. I was only doing an EICR on the one circuit and given where it was just wasn't worth the risk.. I just put it down as an operational limitation.

Glad it wasnt just me that was a bit dim.... :) I have definitely changed with amendment 2 to only using 250v for IR unless I know I have just installed the circuit and there is nothing connected..
 

Reply to IR testing - Checking my logic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
377
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
601
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
308

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock