In the real world, on site, it is often not practical for a L-N test to be carried out as part of the initial verification
Yes, sadly that is the way it is going with most lights being assemblies where you can't remove the electronics from, and where there is not any provision for easily disconnecting it.

I intensely dislike the replace-whole-light-assembly way of the world and would always prefer removable lamps, as it is a waste of resources and adds to testing problems, but for many cases like bathrooms it is hard to get anything IP rated that way.
 
Well I claim to do L-N tests on initial verification each and every time. Not an issue if done at the right time. Seeing Youtubers I get the impression that they wire up/re-wire, fit all accessories the think about testing and that might be becoming more and more the 'norm'. See 641.4 - every installation must be inspected and tested during erection and on completion before being put into service...
 
Well I claim to do L-N tests on initial verification each and every time. Not an issue if done at the right time. Seeing Youtubers I get the impression that they wire up/re-wire, fit all accessories the think about testing and that might be becoming more and more the 'norm'. See 641.4 - every installation must be inspected and tested during erection and on completion before being put into service...
Not doing a L-N test does not mean the installation has not been inspected and tested. There is a compliant LN-E method. How then do you verify you have not caused a low IR L-N after fitting lights/accessories?
The reality is the complication really only applies to lighting circuits, other circuits are simple to test L-N and there is little excuse not to.
 