I've just been looking at a job that has been installed by another company.
One thing I've noticed are the feeds to 2 BMS / Plant panels. They have run in 2 x 150mm 4C and doubled up on the main switch in both panels. No separate CPC has been installed and the banjos aren't earthed either.
If this had been myself I'd have run in a separate CPC and bonded the Banjos.
Thoughts please is this to regs or does it need a separate CPC ?
 

Attachments

  • 20221021_130035.jpg
    20221021_130035.jpg
    284.7 KB · Views: 140
  • 20221021_130030.jpg
    20221021_130030.jpg
    395.6 KB · Views: 89
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?
 
It is unlikely to need a seperate CPC, you need to do the calculation to confirm that though, it is impossible to tell from looking at it. The armour of SWA, especially with 2 in parallel is likely to be suitable as the CPC.

The connection to the banjo doesn't look too good however, they should have at least cleaned the paint off the metal where the bolt connects to it.
What is on the outside of the enclosure? Is the gland and banjo fitted to clean metal on that side?

Hi, the outside is the same as the inside, fully painted. They've just drilled the plate and bolted it down.
 
Is the wire armour earthed the other end?
Might they have used the adiabatic equation (as the armour of 150 sq mm 4c SWA is only 73 sq mm equivalent copper)?
Is the body of the cabinet being used?
What are the earthing requirements of the load?

Not that I'm aware of.
The cabinet is being used as the earth for outgoing Services connected to din mounted earth terminals.
 