Is it ok to have PV system into shared (household) RCD?

So I've had a system installed, but not yet complete/signed off. The issue is that the PV (and a car charger) are wired into a shared RCD (with water heater, boiler and downstairs sockets). When all breakers are on, the system trips. It works when either sockets or PV system are off.

From what i have seen (from my light research), it generally bad practice to be putting the PV (and presumably EV charger) into a shared RCD. Secondly, if it were to be in a shared RCD, then it should be a type B.

Issue is that there isn't space to put anything more into the fuse box, so would require another external box. It may be possible to free up a space if I can replace the door bell transformer with a single size unit.



Inverter: solaxpower.com/x1-boost/

Battery: alphaess.com/smile-b3-plus-3kw-residential-energy-storage-system

Charger: myenergi.com/product/zappi-ev-charger/
 
No it isn't okay because if the rcd trips it can feed back into the other circuits.
Ok thanks - whats the best course of action? Do I need a whole additional fuse-board to accommodate the additional RCD? And does the charger need its own RCD or can it share with the PV?
 
Can you show a picture of your consumer unit.
Here! The 2 on the left are the new additions. The car charger was freed up by putting the downstairs lighting in with the upstairs on the other RCD. Thanks
BAE823BF-3092-4623-A2D9-44CD3DE51957.jpeg
 
Last edited by a moderator:
That's the solar stuff. No idea why it's called that. What makes it incompatible? Would that explain why it's tripping?
It should be a Hager device not Steeple, FB2 would probably mean Fuse Board 2 but that isn't causing the tripping. Tripping could be an excess of leakage from the combined circuits or a fault.
 
It should be a Hager device not Steeple, FB2 would probably mean Fuse Board 2 but that isn't causing the tripping. Tripping could be an excess of leakage from the combined circuits or a fault.
That's what he's been saying - that existing socket circuit had too much leakage and the PV system in addition is too much.
But you are saying it's unsafe and doesn't meet the regulations to be on the same circuit? I want to have a clear plan of what I need to ask for.
I think there needs to be an additional fuse board with an RCD each for the PV and charger? Is that right?
 
That's what he's been saying - that existing socket circuit had too much leakage and the PV system in addition is too much.
But you are saying it's unsafe and doesn't meet the regulations to be on the same circuit? I want to have a clear plan of what I need to ask for.
I think there needs to be an additional fuse board with an RCD each for the PV and charger? Is that right?
No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.
 
No it doesn't need an additional board I would replace your existing board and fit separate rcbos. The PV should not be on a shared rcd the installer should know this although the fitting of the Steeple mcb suggests otherwise.
Yikes, that sounds expensive, no? Is there not another (safe and legit) way? Or am I missing something?
 
Your installer should be providing you with a fully compliant installation.
If it is not suitable to connect to your existing distribution board, they should have come up with a plan that suits you, your budget and remains compliant.
if the 3 things listed above can't be done at quote time, the job should not have been started.
 
Your installer should be providing you with a fully compliant installation.
If it is not suitable to connect to your existing distribution board, they should have come up with a plan that suits you, your budget and remains compliant.
if the 3 things listed above can't be done at quote time, the job should not have been started.
Thank you. Yes I agree and assumed that this was what was happening.
Just hoping there might be another compliant option which would be less costly. Would an additional board with dedicated RCDs not be compliant (and a lot less work)?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Is it ok to have PV system into shared (household) RCD?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
20

Thread Tags

Advert

Thread statistics

Created
jez234,
Last reply from
Risteard,
Replies
20
Views
11,037

Advert

Back
Top