B bathroomboy Mar 3, 2009 #1 Opened an old wylex cu today and there was a 10m cable feeding stand alone breaker for shower fed from live side of main switch together with 25m/m tails is this acceptable practice? myself I would of split the tails.
Opened an old wylex cu today and there was a 10m cable feeding stand alone breaker for shower fed from live side of main switch together with 25m/m tails is this acceptable practice? myself I would of split the tails.
S suburban Mar 3, 2009 #2 Sound like a lash, would not be something I would say is acceptable practice.
L lister Mar 3, 2009 #3 Can't see how they would both fit into the same terminal ........unless they cut a few strands off each, either way not the done thing.
Can't see how they would both fit into the same terminal ........unless they cut a few strands off each, either way not the done thing.
S Spudnik Mar 3, 2009 #4 Its the age old story of 'one point of isolation' for the whole instal, however, many see this as the main service cut out. Anyway, i would remove the 10mm from the wylex, bin it, and put new 25mm tails for the shower cu and 25mm for the main CU fed from a henly block.
Its the age old story of 'one point of isolation' for the whole instal, however, many see this as the main service cut out. Anyway, i would remove the 10mm from the wylex, bin it, and put new 25mm tails for the shower cu and 25mm for the main CU fed from a henly block.