If it is this size could you not take the feed off the loft sockets! or extend into the floor belows ring. Haven't seen may stand alone circuits for a single room on underfloor heating.

I thought any electric 'space heater' be it a towel rad, panel heater or underfloor heating should be on its own breaker?
 
my plan was its own circuit because he told me the heating could pull up to 5kw, so i thought it better to give it its own breaker.
 
will defo consider the spur option if the rating is low enough when i speak to this heating company.
Great idea, think i will offer him a supply & install price on the underfloor heating.
 
i havnt used any underfloor heating before, whats the average size of these for a standard 3x4 room? between 2kw & 3.5kw? if so i could use 2.5mm, make my job a bit easier and cheaper.

If you are concerned about the 2.5mm then why not install using 4mm? 6mm is just ludicrous lol

Has a decision actually been made on which underfloor heating system is being used? If not then wait, use your cable calcs only once all the details have been confirmed:thumbsup
 
isit an underfloor system that just goes as a carpet heater or is he falsing the floor.! theres several good ufh companies online, there spimple and will b so much less hastle getting rid of a third party. all the best with it :)
 
If you want to be sure then I would run from the CU in 4mm, but I would also think 2.5mm spur should be OK for most situations although if you are covering the whole loft it may come up that high but would be unnecessary because it would over heat. Think about putting a 5kW fan heater in a loft... bit OTT
 
Thanks everyone, great help, going to phone him in the morning and put these suggestions to the customer. To be honest i wanted to use 4mm to cover myself but i have half a drum of 6mm left over from another job :)
 
Generally underfloor heating mats are in the region of 150 - 250 watts per square metre, with underlaminate types usually being less.
 