I had an emergency call out to replace a consumer unit, (used a fully 18th edition compliant board) when compiling the installation certificate your not allowed any limitations.

now i know the rest of the house does not need to conform to 18th edition standards but The house is a large house so asides from anything obviously non compliant highlighted in my testing am i expected to ensure 100% of the installation is con formative because i cant with cables being in floors wall and partitions, i also certainly wont be dropping every accessory.

Where do i stand on this?
 
You are not required to make sure the installation in the rest of house is compliant, if you were every board swap would be a rewire for me.

You are required to ensure that all connected and energised circuits are safe. Your testing and cert will demonstrate this.

I suggest you download and read through best practice guide 1, it will help clear a lot of issues up.
 
you need to get readings for each circuit and ensure they are all safe to energise and safe for continued use. they don't necessarily have to comply with current regs.
 
100a main switch, as i am sure you are aware SPD AFD are only a required recommendation unless you can see the need for them in a domestic
100A main switch has been common for consumer units for many years.

Here's the link for the best practice guides
Best Practice Guides | Electrical Safety First - https://www.----------------------------/professional-resources/best-practice-guides/
 
You can’t have limitations on the board

As in you can’t ommit rcd protection for example

The remainder of the house wiring is irrelevant so long as it’s safe for continued use

If it wasn’t safe you probably wouldn’t be changing the board in the first place
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
Business Name
Platinum electrical

Thread Information

Title
Issuing and installation certificate
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
chris day,
Last reply from
Dustydazzler,
Replies
27
Views
3,237

Advert

Back
Top