So...
This is all on my house and no animals were harmed in the making of this hash up but the Mrs doesn't know...yet.
A few years ago we had this house rewired. Usual story, a lash up by an unqualified because we knew no better and it was one of the incentives for me to qualify and offer a better service.
The CCU is an amendment 3, 16 way, split board rats nest but I've completed an EICR, resolved the issues and all was well. Trouble was I hated the rats nest and gave an afternoon to stripping it out, labelling, making sure the L and N were each in the correct side of the board, all tidy and collecting my gold star.

I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?

Apologies for the long story. I have humour where my dignity should be. What are your thoughts on the problem
 
I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?
two rcd in series not good .
 
So...
This is all on my house and no animals were harmed in the making of this hash up but the Mrs doesn't know...yet.
A few years ago we had this house rewired. Usual story, a lash up by an unqualified because we knew no better and it was one of the incentives for me to qualify and offer a better service.
The CCU is an amendment 3, 16 way, split board rats nest but I've completed an EICR, resolved the issues and all was well. Trouble was I hated the rats nest and gave an afternoon to stripping it out, labelling, making sure the L and N were each in the correct side of the board, all tidy and collecting my gold star.

I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?

Apologies for the long story. I have humour where my dignity should be. What are your thoughts on the problem
Have you taken the feed for the W/Shop from an MCB and taken the N from the wrong N busbar? without being there it's very difficult to trace any faults, maybe a borrowed N causing your problems, either that or you have screwed up the connections at the W/S CU.
 
Thanks Guys,

My bet, from what you've said, is that I've got the neutral in the wrong bar. Haven't had time to check but I'm confident that, from the SWA onward is fine. Funny enough, this was the situation that prompted me to asked about labelling in another thread.
 
I dont know about a rats nest but I once found a mouse welded to the incoming main switch terminals of a detached garage CU.
We’ll need a photo of that as quick as you can - we can trade if you like. Here’s mine :
0785DF9C-131D-454C-8C4E-85BD073C0A21.jpeg
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Marti

Arms
-
Joined
Location
Poole, Dorset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Jigsaw Electrical Services

Thread Information

Title
It weren't broke until I got there an' improved it.
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Marti,
Last reply from
static zap,
Replies
20
Views
3,116

Advert

Back
Top