Discuss It weren't broke until I got there an' improved it. in the UK Electrical Forum area at ElectriciansForums.net

Marti

-
Arms
Reaction score
244
So...
This is all on my house and no animals were harmed in the making of this hash up but the Mrs doesn't know...yet.
A few years ago we had this house rewired. Usual story, a lash up by an unqualified because we knew no better and it was one of the incentives for me to qualify and offer a better service.
The CCU is an amendment 3, 16 way, split board rats nest but I've completed an EICR, resolved the issues and all was well. Trouble was I hated the rats nest and gave an afternoon to stripping it out, labelling, making sure the L and N were each in the correct side of the board, all tidy and collecting my gold star.

I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?

Apologies for the long story. I have humour where my dignity should be. What are your thoughts on the problem
 
I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?
two rcd in series not good .
 
So...
This is all on my house and no animals were harmed in the making of this hash up but the Mrs doesn't know...yet.
A few years ago we had this house rewired. Usual story, a lash up by an unqualified because we knew no better and it was one of the incentives for me to qualify and offer a better service.
The CCU is an amendment 3, 16 way, split board rats nest but I've completed an EICR, resolved the issues and all was well. Trouble was I hated the rats nest and gave an afternoon to stripping it out, labelling, making sure the L and N were each in the correct side of the board, all tidy and collecting my gold star.

I have a garage CCU running via 40a type C via SWA to my workshop. One RFC and a light via an RCD.

NOW if I plug in any device in the workshop the 40a type C (at the house) trips with the relevant RCD. IR, polarity and RCD all test fine at the workshop so I've buggered something at the house end. Does this mean I should have been a plumber / pimp / Trump supporter?

Apologies for the long story. I have humour where my dignity should be. What are your thoughts on the problem
Have you taken the feed for the W/Shop from an MCB and taken the N from the wrong N busbar? without being there it's very difficult to trace any faults, maybe a borrowed N causing your problems, either that or you have screwed up the connections at the W/S CU.
 
Some pictures of the inside of both boards may help.

But just to clarify... both the 40A type C MCB AND the RCD supplying it trip, correct?
 
Thanks Guys,

My bet, from what you've said, is that I've got the neutral in the wrong bar. Haven't had time to check but I'm confident that, from the SWA onward is fine. Funny enough, this was the situation that prompted me to asked about labelling in another thread.
 
But just to clarify... both the 40A type C MCB AND the RCD supplying it trip, correct?
That correct SC. the fact that this was working perfectly until I fixed it suggested the issue is at the house end where I tidied up the wiring but double checking all the workshop installation did seem good practise.
 
That correct SC. the fact that this was working perfectly until I fixed it suggested the issue is at the house end where I tidied up the wiring but double checking all the workshop installation did seem good practise.

Does the same occur if you turn the lights on in the workshop?
 
If the MCB is tripping as well as the RCD, then it is likely not just putting the neutral in the wrong bar.

That wouldn't have any effect on the MCB.

Start by doing an IR test on the circuit.
 
I dont know about a rats nest but I once found a mouse welded to the incoming main switch terminals of a detached garage CU.
We’ll need a photo of that as quick as you can - we can trade if you like. Here’s mine :
0785DF9C-131D-454C-8C4E-85BD073C0A21.jpeg
 

Reply to It weren't broke until I got there an' improved it. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, Just done an EICR and all tested fine, until I got to the RCD's. It's a dual RCD board, not sure if it's TNCS or TNS as it's a top floor...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock