Hi Guys had a look at this job today 30 computer stations they dont have computer towers at each desk just a monitor and a box that talks back to the main server going to split the circuits up got to fit a new db and will fit rcbos to each circuit would I be best wiring 20 amp radials or 32 rings there isnt much load. there will be 6 circuits around the room I was going to wire in 4mm te and run a clean earth circuit to each circuit in 4mm singles as this will be for the high protective conductor does this all sound correct.

Normally only do domestic and small commerical work havent wired a ITC suite before as work is dead I need this job and they say there is more through the holidays.

Any help would be great:rolleyes2:
 
If you wire the sockets as RFCs you will not need to add any extra cpc, just use sockets with two earth terminals. If you do it as a radial you'd need to wire a 10mm g/y back from the end - £££s.

Keep the RFCs small with just a few sockets on each. I don't know what the guidlines are but I would have thought it best to try and keep the cpc current down to about 15mA. I find most RCBOs trip at about 23 - 25mA, whereas RCDs seem to be around 27mA.

If you fuse the RFCs at 20A you only need a cable capacity of 12.5, so 2.5 t&e in RM101 (17A) will be fine. Even at 50%, 2.5 is still 13.5A.
 
Thanks when I spoke to the elecsa help line the man said I need to run a separet clean earth to the sockets on the second earth terminal min 4mm
 
if it's a RFC, then you don't need a separate 4mm cpc. that's only for a radial. with a RFC you need to use the socket faces with 2 earth terminals and split the cpc's at the DB into separate terminations. see previous threads for hi integrity earthing.
 

Reply to ITC suite at primarey school in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock