I had one last week, customer had the csu changed last year and now wanting some extra wiring due to building an extenson. I turned up to find a 10 way board which was full, asked for ceftificate while i pop cover to see if any mcb's where used as spares as nothing was lable, found two rings into one mcb, a ring and the garage csu into another maybe a spur i suppose and the best one was 32a for water heater on 2.5mm was fused down at tank.
Then saw the certficate to find ins res. with a n/a on every circuit, n/a for rcd tests, no ring end to end results and zs values all either 0.3 or 0.8