Yea this is the job, it all went quite well really till the phone call, even did a bit of plastering. took about 5hrs ish which im happy about at min.

And havent tried turning all power off, yet, ill investigate tomoz, first thing ill do is check jb, then landing rose then new light, bit dissapointed but i suppose its all learning :)

Thanks.
 
Is the new light that you have fitted good quality, has the internal sensor failed?, i would disconnect your new install and put everything back as you found it, then you will know if its what you have done or not.

Good luck.
 
Is it the MCB or RCD thats tripping?
iF its the rcd / new board and old wiring could be a shared neutral , 2 way landing lights could be the prob.
 
Last edited by a moderator:
Check Switched Live & N connections to PIR they are unlike lights polarity conscious.You maybe dead shorting.
 
Fixed this yesterday. Took switch off and tried resetting mcb and it reset, put another switch on and fine, bit strange but guess they are faulty sometimes :)
 
That is a strange one how a faulty switch can trip an MCB when theres only live's going to it,Never heard of that 1 before:confused:.you learn something new everyday
 
Carl i would go back and check the cables in the light switch you may have crushed the live with the plate screw and now have an exposed live conductor where it was crushed this can be very easily missed. This will blow an mcb especially ir there is no RCD
 
I agree you should look for a damaged live in the switch, this was probably enhanced by the plastering work you carried out with the moisture in the plaster causing the short from permanent live in switch to the back box.

Hope this helps.
 