Kitchen extension, 20m2 on existing 10m2 kitchen, the new area has 5x double sockets, plus own lighting circuit.

My builder has organized the electrics, and I wondered if the arrangement was OK. I am not a qualified electrician (although I am an electrical engineer) and am not familiar with the regs, hence the questions.

The house CU is an old Wylex-style, and so a separate unit with RCBO has been connected direct to the meter tails via Henleys.

This is connected to a 15m-ish run of SWA, along the outside eaves of the house, with separate CPC. The SWA is terminated (haven't looked at how) within an ordinary fused spur unit (which is supplying the lights), and connected directly to a ring supplying the sockets.

The RCBO is rated 20A.

1. Is it OK to connect a ring-wired set of sockets to a 20A rated circuit like this?

2. How can I tell what rating of SWA has been used? My quick VD calculations show that 2.5mm should be OK? I would really like to check what they have actually used.

3. Any other comments?

I am expecting a Part P certificate to be provided, but just wanted to check things through before I pay for the work.

Thanks.
 
This sounds VERY dodgy. Ask your builder for the scheme membership number of the spark and I would recommend that you with hold some of the payment until you receive the certificates
 
This sounds VERY dodgy. Ask your builder for the scheme membership number of the spark and I would recommend that you with hold some of the payment until you receive the certificates

I think I'll get the certificate. However I'd like to know which bits are considered definitely dodgy, as I'd still like to take them up with the builder.

Thanks.
 
Echoing what murdoch has said this sounds quite suspect to say the least. Are you sure it is a ring for the sockets as it sounds like he has run a radial and fused down the lights off of it. Again, ask him if he is part of a competent person scheme.
 
Kitchen ring - just 20A? Kitchen lights and sockets both protected by the same RCBO - not ideal! SWA terminated into fused spur back box - not ideal. You have concerns so the person to direct your questions to is the Spark in question - the vast majority will be happy to talk you through the design and installation. Do you not have a cooker or hob?
 
Kitchen ring - just 20A? Kitchen lights and sockets both protected by the same RCBO - not ideal! SWA terminated into fused spur back box - not ideal. You have concerns so the person to direct your questions to is the Spark in question - the vast majority will be happy to talk you through the design and installation. Do you not have a cooker or hob?

Thanks. Cooker has its own circuit and is in the original part of the kitchen.

So I guess the SWA should be terminated in a little CU, with individual RCBOs for the light and socket circuits? What would then be the recommended arrangement at the meter end of the SWA?

Thanks again.
 
From what you have described above, it sounds like doggy Dave is doing the job!! But you know that already though don't you, otherwise you wouldn't be here asking?? No better way of putting it, ...It's a crap job, end of!! lol!!

Why might i ask are you not changing the the old 3036 CU for modern RCD protected CU that will protect the whole property?? £300 to £400 well spent of anybodies money and a damn sight better solution than the abortion it seems you're paying for at the moment!!
 
How do you know the sockets are wired in a ring? (you said you didn't investigate the swa at spur).

Looks like the electrician has limited the circuit to 20A to keep the swa at 2.5mm - was there a significant cost pressure on this job?

How do you know the separate earth cable is a CPC? More likely a main bond to something.

Are these 5 sockets for worktop use or for appliances?

Was there a good reason for this guy having to run the swa + earth around the outside of the house?

Is the lighting the 'under unit' type or on the ceiling?


You seem to know a lot of 'sparky' terminology for an electrical engineer eg henleys, cpc, CU etc - sure you're not a Electrical Trainee getting us to check out something that YOU'VE done??? :)
 
Last edited by a moderator:
How do you know the sockets are wired in a ring? (you said you didn't investigate the swa at spur).

Looks like the electrician has limited the circuit to 20A to keep the swa at 2.5mm - was there a significant cost pressure on this job?

How do you know the separate earth cable is a CPC? More likely a main bond to something.

Are these 5 sockets for worktop use or for appliances?

Was there a good reason for this guy having to run the swa + earth around the outside of the house?

Is the lighting the 'under unit' type or on the ceiling?


You seem to know a lot of 'sparky' terminology for an electrical engineer eg henleys, cpc, CU etc - sure you're not a Electrical Trainee getting us to check out something that YOU'VE done??? :)


I saw the sockets being wired at first fix, and it appeared they were in a ring.

2 sockets for worktop, 1 TV (high on wall), and the other two are undefined.

There was no obvious internal route (converted bungalow, laminate upstairs flooring), and so the external route was basically to save time trying to find one.

Lighting is ceiling/wall.

A long time ago I used to do my own electrics (think red/black/green insulation days), but I am not at all up to date with current regs - that would be a lot of studying to understand something I couldn't do if I wanted to because of the Part P restriction.
 
If the electrician has wired the sockets in a ring (though it may only have appeared that way) then that is odd, especially when you consider how busy the FCU will be.

But I fail to see how this installation as described is as 'bad' as everyone seems to be saying -

It's a 20A radial feeding 5 comparatively low loaded sockets in the extended end of a kitchen.

The fact that there is swa connected to a spur back box is not a biggy (had to switch from swa to pvc somewhere).

The fact that sockets and light are on same RCD is not a biggy (just at the extended end of the kitchen)

The fact that lighting is spurred from the sockets at that end of the room is not a biggy.


Don't get what all the fuss is about - the electrician may have had reasons/limitations imposing all of this.
 
Last edited by a moderator: