Hello everyone, I'm writing to you for a bit of advice on a private job I am doing for a family friend.
I am a qualified spark and have been working for a company for 3/4 years now.

The new kitchen will have 6 new spots, 6 new sockets, under cabinet lights, led strips, a new cooker and hob feed. The fuse board is quite old, so will need to have a separate small fuse board for the kitchen correct? But I wish to come of some existing feeds from existing sockets and lights. Rcd?
There is a basement which makes life a lot easier as I can run cables underneath and simply poke up my cables underneath as it is easily accessible. Even have the board under there too as the client is happy to have it their.

just wanted some advice on how to go about this job, etc (what I should do about the board), (cooker feed), how much I should quote price wise?

Surprisingly I haven't really worked on fuse boards a hell of a lot, due to my company being quite big, and them not letting the younger sparks have a go.

would be much appreciated if anyone could pass some advice on, also if anyone knows of any good websites for light fittings and led strips.

Thanks
 
can't help thinking that now would be a good time to upgrade the CU to RCDs but it sounds like you are not really experienced enough for that?
 
To be completely honest no I'm not experienced enough to change the fuse board over, but I can pretty much do everything else. I haven't really dealt with fuse boards that much, that's why I would Like some help.
I thought I could run a 6mm cable for the cooker and run new lighting feeds and socket feeds to a new board.
 
Check out what the rating is of the cooker first, don't just assume 6mm will cover it, although in most cases it will. Sorry I can't help more, not really my territory!
 
have a look if you can retro fit some rcbo`s into existing board?
another option may be changing in into a modern one. Or if its a big house then armoured sub-main in the basement to the area under the kitchen and running circuits from there. You will need a 32 ring for sockets, and 32 radial for the cooker.
if there is new built will be nice to have lights on new circuit too. have a look for lights at tlc electrical wholesalers, they got nice shiny catalogue with prices printed, pass it to the customer let them choose...nice selection and good quality too.

edited: this job will need messing around in the fuseboard. if you not feeling competent in the field then leave it for someone who will know what they doing...
 
To be completely honest no I'm not experienced enough to change the fuse board over, but I can pretty much do everything else. I haven't really dealt with fuse boards that much, that's why I would Like some help.
I thought I could run a 6mm cable for the cooker and run new lighting feeds and socket feeds to a new board.

If you are not experienced enough to change a fuse board over, should you be putting in an extra board ?
Does your experience stretch to the testing and certification that this job will need ?
As Murdoch asked, how will you be notifying this to building control, a legal requirement ?
 
To be completely honest no I'm not experienced enough to change the fuse board over, but I can pretty much do everything else. I haven't really dealt with fuse boards that much, that's why I would Like some help.
I thought I could run a 6mm cable for the cooker and run new lighting feeds and socket feeds to a new board.
so...you means to say that you have been with this outfit for 4 years...and they havn`t let you at least help install a dis-board?.
thats shocking...
 
You may be attempting more here than it may be safe for you to undertake, you say you cannot change a consumer unit, however the work is very similar for fitting a consumer unit, so you could well be out of your depth here.

An easy approach would be to consider the kitchen as separate from the rest of the house and run sufficient new circuits in compliance with the current regulations from a separate consumer unit to supply the kitchen in its entirety.
Then you avoid having to upgrade any existing circuits or consumer unit. It is a bit of a bodge since the board could usefully be changed, but this would entail further work.

Take great care in what you are doing and consider getting in someone to assist you rather than attempting it alone.
You do need to consider the cable calculations required rather than just saying I will use a 6mm² for the cooker (this is very likely to be OK but have you checked it will be OK?)
 
The fact that you need to ask about so many basic elements of this job worries me. Qualifications mean nothing really without at least some experience working on this type of project.
Firstly, would you consider yourself competent to carry out this work, along with all testing required? Secondly, when you hit problems due to inexperience, are you prepared for the trouble it will cause between the owners and your family?
 
Why would you run in a separate CU just for the kitchen, when the main CU is obviously in need of upgrading?? Especially as you point out that wiring from the original CU position is going to be as you put it, ...easy!!

I take it that all this work is for a new kitchen install, so it makes sense to upgrade the original CU for the whole house at this time with a dual RCD board or an all RCBO CU...

If as you say you're a qualified spark of 4 years, a CU change should not be much of a challenge to you, ....hell if 17 day and electrical trainee wannabe's can do it, you damn well should be able too!! But then, are you registered with any of the scheme providers, because if you're not, then you'll have go through the LABC, and that's going to cost a bit of cash!!
 
Last edited by a moderator: