Stroppy

I am currently ripping apart a kitchen for a rewire which is being knocked through into another room to turn it into a kitchen-diner.

Being a 16th Edition installation we have the following arrangement of relevant circuits on the split board:

a 2.5 RFC for the sockets on the RCD side

On the non-RCD side:

4mm radial for fixed appliances
6mm radial for cooker
6mm radial for hob
1mm radial for lights

The customer now wants underfloor heating installed as well, which we are told needs a 20A supply, so bearing in mind running in a new circuit back to the already full consumer unit is not an option, my proposal is to use the 2.5 RFC for the sockets AND fixed appliances (as they won't be a huge load) and 'donate' the 4mm radial to the underfloor heating.

The existing double-pole switch in the CU for the non-RCD circuits will be replaced with an RCD, to protect the radial circuits. I did wonder about RCBOing these circuits, to avoid interfering with circuits I am not altering, but it seems silly to change 4 BS1361 fuse carriers for RCBOs leaving only two unchanged, when it will be easier and cheaper to change the switch with an RCD.

What would our panel experts do?

(before you call me an idiot bodger, read my disclaimer below!)
 
Considering the fixed appliances have a circuit all of their own I'd question the "won't be a huge load". What fixed appliances exist now?
 
I would leave the appliances seperate and also if the wiring is surface or in steel pipe I'd avoid an RCD to that circuit, I wouldn't have my kitchen appliance ring on an rcd haha, too much money in the freezer.
 
or henley block a 2 way CU with RCD and MCB in for the UFH. this will leave a spare way for future use.
 
What underfloor heating are you using, how large is the area, have you checked what the actual load is going to be, 20A seems a lot unless its a very large kitchen, or mabe the diner part of the room is being heated as well?.
 
The fixed appliances will be:

Microwave
Dishwasher
Wine Fridge
Fridge/freezer
Extractor fan

so yes, maybe not as light a load as I was hoping!

Good point about the single point of isolation, StuartCourt.

Surprisingly for a domestic kitchen the wiring won't be surface or steel conduit!

I would love to put a separate CU to sort all this out, as the existing CU has been extended to accomodate two more circuits than it is designed for, but there is not the phyiscal room in the cupboard for blocks and another one, nor to put in a bigger single CU.

The UFH is being subcontracted out, and yes the diner part is being heated as well. From memory the area will be about 7m x 4m, excluding the areas under the units of course, coming to around 25 sq m. If they decide it can run off a 13A FCU then I'll be laughing as it can live on the RFC and I can keep my fixed apps radial.

If it is 20A apparently I'll have to wedge some contactors in somewhere as well, as their stats can only take 13A.
 
as has been said...leave them fixed appliances on their own....you dont want to lose all the downstairs points do you if something developes excessive earth leakage do you...better to have some diversity here
 
Leave the '16th' side as it is if you can and load permitting run your underfloor heating from an fcu on your rcd protected ring, suitably labelled at the cu. What is the power rating on your heat mat(s) and what is the existing demand on the ring?
 
Last edited by a moderator:
ufh is usually around 100watts/sq.m., so that should run off a 13A FCU.
 
If it can run off an FCU I will be laughing as things can mostly stay as they are. The UFH install is being subbed out, so I'm not sure what they'll be using.

Existing (and proposed) demand on the ring will be the kitchen-diner only, viz: 5 double sockets for the kitchen side, and three on the diner side.
 
i'd be more inclined to combine the hob & oven feeds into 1 circuit if i had to free up a spare way.
1 cooker switch can feed 2 or more cooking appliances so long as they're within 2 mtrs of switch.
and its easy to fiddle the diversity figures to suit the job ;-)
 
You need more info on UFH but i suspect you will be able to run as above post suggests (Rob Smith )
 
I was just thinking about stealing a cooker circuit, Biff. The hob is 4.7kW, but I don't know what the oven will be.
 