Hi guys read plenty of things on these forums and now have a problem to post...
Fitted a fan heater to a spur in a bathroom today. The spur is on 16A breaker and appears to be a radial. Fitted and switched on at DB and spur but no luck.
When i tested the spur I had 240v between line and earth, 12v between line and neutral and then 120v between neutral and earth.
At this point I isolated the circuit thought I’ll save that one for tommorow so just wondering has anyone experienced this before as I’ve never come accross this before
 
Hi guys read plenty of things on these forums and now have a problem to post...
Fitted a fan heater to a spur in a bathroom today. The spur is on 16A breaker and appears to be a radial. Fitted and switched on at DB and spur but no luck.
When i tested the spur I had 240v between line and earth, 12v between line and neutral and then 120v between neutral and earth.
At this point I isolated the circuit thought I’ll save that one for tommorow so just wondering has anyone experienced this before as I’ve never come accross this before
What you meant to say was I tested it couldn't make head nor tail of the results, so I'll ask on here and go back tomorrow with the answer.
 
As above and above the other one Floater and nobody likes a floater!!!!!
 
What you meant to say was I tested it couldn't make head nor tail of the results, so I'll ask on here and go back tomorrow with the answer.

Ok your one of them.
Been sparking 10 years and never asked anything on a forum got a strange one today and thought I’d share it.
Thanks for any other sensible responses
 
Ok your one of them.
Been sparking 10 years and never asked anything on a forum got a strange one today and thought I’d share it.
Thanks for any other sensible responses
Been sparking for 1o years? matey I was Sparking as you put before you was born
 
Been at it a long time but had to look up how to wire a 2way cct when both supply and lamp feed are in same switch.......never wired them like that and never come across it as dont do much domestic.........so to be helpful if you are measuring L-N on output side of FSU could be poorly FSU neutral side, if you measured it on the input side then would trace cct back to breaker and find the neutral and test
 

Reply to L-E 240v L-N 12v N-E 120v in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock