Landlords Visual

Discuss Landlords Visual in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

G

Graeme Harrold

Just been to a property today to complete a visual inspection and found a couple of nice surprises -

- 32A ring with 4 terminated cables - out of curiosity I did end to end r1 which showed continuity on 3 cables

- Shower supply taken from supply side of the main switch, through chocblocks and off out to a 63A 30mA RCD......

Hopefully I get called back to sort these out.....:eek:
 