some advise in case I'm missing something obvious just fitted 3x 400watt floodlights on there own circuit 6 amps , type b . Connection checked and ok, tripped every time switched on , should I change the mcb to a type c .?
 
did you conduct a schedule of tests....?
in fact any testing at all of the existing?

if all tested and OK then it sounds like inrush....

go for a C curve (as long as Zs is good for it)...
 
Does it trip immediately with the accompanying bang, or is there a slight delay before it trips and just with the noise of the breaker switching off?
 
And what type of lamps? E.g. for 3x 400W SON on EM ballast 6A won't be enough. If tungsten then OK on 6A except for inrush as post above. Pls confirm IR results in MΩ.
 
Start up current on 400w floodlights could be as high has 1500w per flood! Check manufacturers details for info. C10 needed I would say.
 
and guess what...

we still havn`t been told by the O/P what his measured value of Zs was...furthest point....

as theres a few in here just advocating going from a 6A to a 10A...without considering disconnection times....

or should we just rely on an RCD?
 