I was picked up by one of our wounderful inspectors for allowing something like this to pass as I had failed to apply reg 314.1 (i) "avoid danger and minimize inconveinience in the event of a fault". Lose the ring lose the lights.
My location was a converted 40foot ISO container into 4 bedrooms. One 20A 2.5mm ring with S/FCU's doing the lights my argument was that they would be asleep and wouldn't matter or if awake they would be able to find the door as they would know where all the potential trip hazards were.
Not good enough.... BS7671 violation and written up !
 
I was picked up by one of our wounderful inspectors for allowing something like this to pass as I had failed to apply reg 314.1 (i) "avoid danger and minimize inconveinience in the event of a fault". Lose the ring lose the lights.
My location was a converted 40foot ISO container into 4 bedrooms. One 20A 2.5mm ring with S/FCU's doing the lights my argument was that they would be asleep and wouldn't matter or if awake they would be able to find the door as they would know where all the potential trip hazards were.
Not good enough.... BS7671 violation and written up !

Interesting decision, and the right one IMHO.

Too many posters on here are trying to ignore the reg and fit a single up front RCD which doesn't really comply - however in a "garage" type situation I'd RCBO the sockets and surface/trunking run all the lights then a MCB is OK!!
 