Hello all, I need a bit of help please!! Got a problem with lighting in a school classroom. 9 x double prysmatic flourescent tubes and apparently the lighting MCB keeps tripping randomly. Any ideas what this could be? I changed some of the older looking tubes and uprated the breaker from a 6amp to a 10amp - the thinking behind that is that as the fittings age and detoriate they pull more current (a colleague suggested this). Thoughts and opinions please! Thanks
 
open them up and have a look prob a ballast on the way out or a burnt wire usually the wire that passes the ballast inside the fitting burns up with the heat coming off it , not hard to spot
 
drop the MCB back down to a 6A...but go for a C curve....check Zs is good for it though first

i mean is it doing it on startup?

you know the formula for flourescents dont you....Ib X 1.8 for inrush...
 
it's time to get the tester out sparky as there is clearly a fault, and I don't think it is very good advice to just up the mcb from a 6amp to 10amp to stop it tripping, as you are then altering the design spec for the circuit zs etc, as above it is probably a faulty ballast but never just up the mcb rating, that is like removing bypassing an rcd to get round a fault.
 
When designing commercial and industrial lighting circuits we always allow 1 amp per fluorescent, however that said the 9 twin fittings you have now tripping a 6 amp is probably due to a faulty capacitor which is shorting out the supply in one of the lights as they are wired in parallel across the main feed and neutral conductors and can blow fuses or breakers if faulty, JMO
 