Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.
End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm
IR >1000 Mohm
There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
N 0.21Ohm
E 0.02 Ohm
IR >1000 Mohm
Any one any ideas?
Poor connection on your MFT?
Nope. Checked it half a dozen times. same result. Checked it with my other mft, same result.
Excuse me for silly suggestion (just a trainee) but no parallel paths like cable armouring (I know you said T+E, just trying to have a go at helping) :willy_nilly:
They haven't put in a 10mm CPC in the T+E have they?
Honestly this defies logic. You obviously have a ring on your r1 rn and so by rights your smaller CPC should be higher on r2.
All I can think of it start to break the ring down, it's only 4 sockets and test the cable from CU to Socket 1 and then Socket 1 to 2 and go round the ring
Reactions: 1 person
Thanks for the replies.
(Hightower) No parallel paths. End to end on drum, I will try that. It was a new 100Mt roll.
(Steve) It's a double garage, the CU is in the garage. so total ring about 15/20mts? They are fixed to a breeze block wall.
(malcolm) Will do, I will be going back there next week to finish off, so I will try that.
Metal sockets? if so remove the front plates from the back box and dis the fly lead (if you have one) and re test r2
Right just checked the rest of the roll.
L 0.37
N 0.37
E 0.67
Which is what you'd expect. So why it is down on the install I'm stummped.
Pete, yeah will try that also.
L 0.37
N 0.37
E 0.67
Have you responded to post 10 yet?
Sorry wrote it out then got sidetracked.
Please do I'm clutching at straws but I may be onto something
Reactions: 1 person
It looks like I might be up there on Saturday so will try things out then.
I will post back