I reckon the wall is damp and the low reading is via the 'fabric of the building' with metalclad sockets being used.

See post 10 I asked the OP to remove socket fronts and fly leads and retest he is going back Saturday to do just that.
 
Hi all.
Didn't have time to do any electrical work on Saturday. Was helping him move all his stuff from the old house.

Dave & Matt. Yes I wondered if it could be the building that was bringing it down, but I had never come across it before.
 
I agree with Pete and Dave - the sockets and backboxes will all be earthed, but also there will be some kind of parallel path via the mass of the building, like with a TT system. The building won't even need to be particularly damp for this either. As Pete says you could disconnect all the flyleads and leave the socket fronts hanging in mid air and test to prove this, but a low R2 is a good thing.
 
Damp? What's it damp with, mercury? A dripping wet wall might get you 0.02 MΩ but not 0.02Ω. Taken at face value (which is not always right with 1 s.f. on low resistance tests) 0.02Ω is equivalent to about 1.5m of 1.5mm², so the socket boxes are probably connected directly together with a large chunk of metal. Perhaps the fixing screws have gone through metal studwork or a plaster bead or similar.
 

Reply to Low R2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Been to a fault finding job and lights where tripping the rcbo. After further investigation we found that it was a blue strapper cable (old...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock