Hi peeps. Doing an end to end test on a ring final circuit.
R1- 0.43
RN- 0.44
R2- 0.33

Its old stranded 2.5, seems to have about 7 stands on the live n neutral conductors, and about 4 strands on the cpc conductor.

Why is the r2 lower than the r1 & rn!!

HELP
 
Hi peeps. Doing an end to end test on a ring final circuit.
R1- 0.43
RN- 0.44
R2- 0.33

Its old stranded 2.5, seems to have about 7 stands on the live n neutral conductors, and about 4 strands on the cpc conductor.

Why is the r2 lower than the r1 & rn!!

HELP
Well you had had one answer, but I wonder do you have an opinion why?
 
old stranded 2.5

Not likely, expect it to be 7/.029 which normally has 3/.029 CPC. SO when you calculate what you expect R2 to be, remember the ratio of resistance per metre will be would be 7:3 not 2.5:1 or 5:3. IIRC there has also been 7/.029 with 3/.036 CPC.

about 4 strands on the cpc

4 ?! Are the numbers 1, 3, 7, 19, 37 familiar at all?
 
Hi peeps. Doing an end to end test on a ring final circuit.
R1- 0.43
RN- 0.44
R2- 0.33

Its old stranded 2.5, seems to have about 7 stands on the live n neutral conductors, and about 4 strands on the cpc conductor.

Why is the r2 lower than the r1 & rn!!

HELP


Same as post 5,4,3 and 2
 
Surley parellal paths wont be a factor when disconnected from the earth bar?

Could be!

eg. you have 5A lighting sockets and ring main sockets fixed together. So if the metal back boxes are earthed by their respective cpcs, from one position to the next will be 2 cpcs in parallel.

You could also measure r1, rn and r2 at a socket location, and you might get different measurments because of the measurement position in respect to the parallel paths involved.
 
Surley parellal paths wont be a factor when disconnected from the earth bar?

For example, if you have more than one item of equipment on the circuit with a connection to water/gas pipes, then you may have a parallel path that is very low resistance. For example a gas boiler, a gas hob with electric ignition, etc.
 
Last edited:

Reply to Lower r2 end to end reading than r1 & rn in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock