If you are still on Supermarkets,
The door release signal drops out the relay mounted local to the Fire/smoke doors to close them.
The same signal Opens the shop front auto doors.

And where used, releases the Maglocks on external Fire escape doors and roof access doors

And opens the Radfords barriers(gates) and shuts down AHU 1, 2, 3, etc.
 
Smoke vents too or are they operated manually.

Depends, Generally all circulating air fans will be shut down on a fire alarm (except fire escape stairways, that need to be kept pressurized) Smoke extraction exhaust fans would normally be under the control of the attending senior fire officer, normally from a strategically located firemans control panel!!.....
 
If the control is next to the fire panel, you will find the relays or contactors will have 24v coils, so the aux 24v on the panel will be passed through fire relay to you control relays
Roller Shutter.jpg
 
Now when went to fix this this morning , I got told todo something else . The guy told me it's wrong contactor as rated at 400v . Anyway
 
Think the guy said they taking 24v from sliding doors to power the unit . Then white fp controlling contactor .. But the contactor had 400v coil , so needs changed. Did this sound right
 
Hochiki addressable relays, rated 5amp per contact, they are mains rated relays.....but will be all down to how they have been programmed, presume panel in MX or Morley
 