Hi all,

just took main protective bond (10 mm) to water pipe which is of the old lead type.

Main bond length is about 4 meters.

Cross bonded to rads and sink(utility sink)

Then did R2(using 2.5mm) to pipes under the kitch sink.

Reading was 0.10 ohms.

regs say max allowed value is 0.05.

This reading seems a bit high.Anyone got any reasons for this(plumbers joints,lead pipe,or 2.5 R2 lead) and would it be acceptable.

Need to know as Napit assessment is due on the start of June...............
 
possibly resis of test leads or poor connection,can you see the run throuhout its length? theres no value to mark up, just prove continuity exists
 
0.05 is the limit, but you dont have to give a value.
when you did your continuity reading did you deduct the resistance of your 2.5 test lead?
also you shouldnt be teminating onto lead piping mate
 
There is no requirement for contnuity between the main bond at the stop**** and pipework/sink in a kitchen ,so it can be open circuit and still comply with the regs......cant see why you are testing it.As long as your main bond is on the consumers side of the stop**** and before any branch pipework,thats all that matters.
The 0.05 ohms is continuity between the MET and main bond position.
 
Last edited by a moderator:
Agree with wirepuller....the 0.05 value is for the resistance of the actual bonding conductor from the MET to the earth clamp.
 
Cheers fellas, i know what i've done......school boy error.....Didn't subtract the resistance of the R2 lead.:o.

With the assasisnation sorry i mean assessment coming up i'm thinking way to much into things.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Main bonding value
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Mr.Black,
Last reply from
ezzzekiel,
Replies
7
Views
5,613

Advert

Back
Top