R

rick

Hi all

Found this today (in my own house) ... main bonding goes from CU to gas and water... but found after lifting boards that first run from CU is jointed in an earth block under the floor, from where it goes separately to gas meter and stopcock.

I know this is not to regs and will replace it, which will be a right PITA - but out of interest what would you grade this on a PIR (I don't do PIRs)

And why don't people do things properly the first time around :-!

Cheers

Richard
 
Most likely a 2, especially if it's a TNC-S, as the single conductor that then splits into 2 conductors would most likely have insufficient CSA, unless it started off as a 25mm.

If it were TN-S or TT and started life as a 16mm and then went off in 6mm.......................you may have to make a judgement call

Then though it would be a code 2 for the in-accessible joint under the floor, the joint not being adequately protected, or mechanically sound just flopping about, so if I saw a code 2 for that I wouldn't be arguing about it to be honest.
 
Last edited by a moderator:
or you could make the block a MET, as long as it's accessible.
 
Most likely a 2, especially if it's a TNC-S, as the single conductor that then splits into 2 conductors would most likely have insufficient CSA, unless it started off as a 25mm.

If it were TN-S or TT and started life as a 16mm and then went off in 6mm.......................you may have to make a judgement call

Malcolm not sure what your reasoning is here regarding larger size conductor.

This is a domestic and if TNCS, if 10mm from CU to earth block and then 10mm to water and gas then thats Ok wrt to sizing, but still agree code 2 if joints not acessible. Although if pulling the floorboard up is easy and a diagram/note made at CU I could be persuaded otherwise.
 
Malcolm not sure what your reasoning is here regarding larger size conductor.

This is a domestic and if TNCS, if 10mm from CU to earth block and then 10mm to water and gas then thats Ok wrt to sizing, but still agree code 2 if joints not acessible. Although if pulling the floorboard up is easy and a diagram/note made at CU I could be persuaded otherwise.


That is true YM, there is nothing to stop you daisy chaining, ie MET to Water and then Water to Gas all in 10mm......so stand corrected.

I put it down to a senior moment and thinking about a combined CPC/bonding conductor.....................well that is my excuse and i'm sticking to it lol
 
If its ALL in 10mm, why not just run another tail to under the floor, and then crimp them.

I have an external bonding job to do through a torturous conduit route.

There is no way on this earth that it will go in in one go, so will have a couple of crimped and soldered joints in the through boxes.
 
the cable from CU to the block could you not crimp it so its going to the gas meter seperately and add a bit of 10mm earth and crimp that too for the stop cock,you will have 2 10mm earths then job done!!
 
That is true YM, there is nothing to stop you daisy chaining, ie MET to Water and then Water to Gas all in 10mm......so stand corrected.

I put it down to a senior moment and thinking about a combined CPC/bonding conductor.....................well that is my excuse and i'm sticking to it lol
of course not Malcolm...but bonding conductors should then be either crimped...or kept continuous when daisychaining..from one extrainious point to another.....not the case here....
 
Thanks for all the input - I always like to return to a thread when the job is done, so... what I have done is taken the run from the CU to an earth block, which I have put in a 2G box in a cupboard with a blank plate over and labelled up accordingly for test and inspection. From there, two easy runs to where the old inaccessible block, was and crimped to both existing cables with heatshrink over.

Guitartist FYI TNC.

Thanks again for all posts!
 