axel132132

Hi,

I have just been and looked at a house for my mate, he has a earth rod in his front garden which has a 4mm cable from it to the mains board. OBV this is too small..

What are the solutions as this rod is no longer accessible - he paved over it >,<


I was thinking maybe putting a new ROD under the mains board under the floor boards, BUT i read abit about hitting water mains and gas mains how do you know were the water or gas mains are!..

Also is there any other solution? Get Electric Board in or anything

Cheers All
 
On a TT system a 4mm earth is adequate, check your regs!. Does the rod have good readings still? I think the idea of a new 5/8th rod , in a nice placcy pit is a good one though
 
You could ring to see if a PME conversion is available but if not, select your new rod position and dig down a way to see if there are any incoming services. If not grab yourself a couple of coupleable 5/8 rods and start whacking.

- - - Updated - - -

Why is it obvious that the 4 mm isn't man enough for the job?
 
4mm earth on tt system is fine what was Ra reading? just dont like the fact its inaccesible would check with dno if pme is available before whacking in new rod
 
You'll be able to check and see if PME is available by walking to a couple of the pole lines, I think its about every 3rd one that they put the system type on them, well they do around here anyway :)
 
Hi,

I have just been and looked at a house for my mate, he has a earth rod in his front garden which has a 4mm cable from it to the mains board. OBV this is too small..

What are the solutions as this rod is no longer accessible - he paved over it >,<


I was thinking maybe putting a new ROD under the mains board under the floor boards, BUT i read abit about hitting water mains and gas mains how do you know were the water or gas mains are!..

Also is there any other solution? Get Electric Board in or anything

Cheers All
Have you checked to see if it is actually too small?
 
Hi,

I have just been and looked at a house for my mate, he has a earth rod in his front garden which has a 4mm cable from it to the mains board. OBV this is too small..

What are the solutions as this rod is no longer accessible - he paved over it >,<


I was thinking maybe putting a new ROD under the mains board under the floor boards, BUT i read abit about hitting water mains and gas mains how do you know were the water or gas mains are!..

Also is there any other solution? Get Electric Board in or anything

Cheers All
did you get a Ze here by any chance?...
or is this another one of those `let me see` threads.....where a piece of test gear hasn`t been anyware near the install....and us lot in here are supposed to just do a bit of `guess work` on your behalf?
well i can tell you now i`m not for guessing....
go away....get a Ze for a start
 
Hi,

I have just been and looked at a house for my mate, he has a earth rod in his front garden which has a 4mm cable from it to the mains board. OBV this is too small..

What are the solutions as this rod is no longer accessible - he paved over it >,<


I was thinking maybe putting a new ROD under the mains board under the floor boards, BUT i read abit about hitting water mains and gas mains how do you know were the water or gas mains are!..

Also is there any other solution? Get Electric Board in or anything

Cheers All

Do you own the equipment to check the Earth Rod and do you know how to use it...with respect, you should utilise that knowledge and equipment before coming on here and asking people these questions. if you posts that question AFTER doing the checks and posting the results with your question, and your simply checking to see if your thinking is correct, then that is fine, but it's a bit rich expecting others to think for you.

Bear in mind even if you install a new earth rod you will need to check it is compliant and you have a satisfactory result...just hammering one into the ground, attaching a cable and slapping yourself on the thigh as Job done is not acceptable.
 