HI Guys

I have a 8 flats and 2 retail units due to be built soon and i am trying to work out the Maximum demand for each of the flats and the 2 shops so the supplier can ensure a large enough mains supply.
The Retail units are to just have a supply to a distribution board, the shop is not too large and without any definite future spec given to me i would assume a 16mm 4c SWA 3P+N would be adequate.
The flats are of differing sizes but i have done the calcs and worked out the correct sizings for the space to be heated.
If i allow diversity for the final circuits and taking the storage heating at 100% the total max demand is between 123A and 164A! In every property ive been in storage heaters are fed from the same supply as the Consumer Unit but via a timeswitch thereby still using the one EP fuse 60A-100A.
Would the flats require 2 feeds or could this still be achieved with the 1 supply as the storage heating would not come on untill midnight?
 
To be honest I have yet to see an economy 7 installation and normal installation having separate supplies. 99% would be as you described either utilizing a time clock, or as now we have a dual meter, with the one 240/230 supply.

You may find that it would be 80-100amp rather than a 60amp which most flats would utilize quite easily. No I doubt very much you need 2 supplies unless there are other high load demands on the installation
 
Thanks Malcolm

I was planning on using a 25mm SWA 100A supply with a dual E7 meter at the meter cupboard thereby using only a single supply, a timeclock at the CU controlling a contactor for the heaters.
Thanks
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Max Demand calc for new supply
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
leestaf,
Last reply from
leestaf,
Replies
2
Views
1,295

Advert

Back
Top