I find it odd that the incoming water supply isnt plastic..... only come accross half dozen lead ones in 17 years

Likewise I have only come across a handful of lead water mains still in service. But I have come across plenty of iron/steel ones.
[automerge]1598132114[/automerge]
I may have missed it, but I don't see anywhere where the OP has told us what the earthing system is yet, and nobody appears to have asked.

If it is TT or TNCS then it likely is OK with a 6mm main bond.
 
System is tncs and it is copper coming out of a floor board at the rear of the house. I could go ripping these up but wasn't going that far on a quote for obvious reasons. Could be anything coming in, I can't see, jouse is victorian
[automerge]1598171927[/automerge]
Is it done the way the regs say? No
Is it achieving the goals of the regs? Yes
When comparing the do-nothing option of leaving the old Wylex rewirable CU in place with no bonding, with a replacement RCD/RCBO-based CU and a bonding-by-pipework option, I would have say it is a massive improvement in safety.
This is my thinking, its one of those situations where it'll probably all get left an old mess
 
This is my thinking, its one of those situations where it'll probably all get left an old mess
That is why I would probably see if good gas supply bond & supplementary bonding of hot/cold/gas pipes where accessible is enough to measure the water pipe as well-bonded. It might not follow the specific guidance to the letter, but it does the necessary job.

After all, if you did an inspection and found no sign of water bonding but it measured 0.05 ohms to the MET, how would it be coded? C3 at most. From the best practice guide:

C2 for: Absence of effective main protective bonding of extraneous-conductive-parts entering the premises

C3 for: Main protective bonding to gas, water or other installation pipe is inaccessible for inspection, testing and maintenance, or connection not made before any branch pipework.

My emphasis on the "effective" aspect. Not doing the upgrade to an RCD/RCBO board in my mind is far more dangerous than leaving as-is, so insisting on by-the-regs water bonding that the customer will reject would be a case of perfection as the enemy of good.
 
Likewise I have only come across a handful of lead water mains still in service. But I have come across plenty of iron/steel ones.
[automerge]1598132114[/automerge]
I may have missed it, but I don't see anywhere where the OP has told us what the earthing system is yet, and nobody appears to have asked.

If it is TT or TNCS then it likely is OK with a 6mm main bond.
Why the emphasis on TT and TNCS?
Why would 6mm not be ok with TNS?
Did you mean it's ok with 6mm for TT and TNS? 10mm for PME.
 