Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and newly decorated walls, coving and so on) and the mains water is opposite side of the house. Although the strap isn't visible I have run a wander lead and got 0.29 on a 6mm at the dB to the stop cock so it is bonded. I know its not a good reading but wonder what peoples opinions are in changing the board? There is no way they want the work done if it involves ripping the house apart for the water bond but they are more than happy to do the board and gas.
 
Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and newly decorated walls, coving and so on) and the mains water is opposite side of the house. Although the strap isn't visible I have run a wander lead and got 0.29 on a 6mm at the dB to the stop cock so it is bonded. I know its not a good reading but wonder what peoples opinions are in changing the board? There is no way they want the work done if it involves ripping the house apart for the water bond but they are more than happy to do the board and gas.
.29 ohms = 94m of 6mm cable, or more likely a loose connection. Could you not run the bond around the exterior of the building?
 
is there a gas pipe anywhere near the water stop cock, or could the water bond be connected elsewhere ( as in as close as practicable to the incomer without demolition)?

another solution would be to get a wet-pants to fit a plastic section close to the stop cock
 
.29 ohms = 94m of 6mm cable, or more likely a loose connection. Could you not run the bond around the exterior of the building?
I know its really high and realistically only a 20m run, its a terrace with board at the front and stop cock at the back, gas meter i van do externally but no chance on water
[automerge]1598034761[/automerge]
could you elaborate on how you tested this please? was this tested with the 6mm disconnected from the MET?
Yes so I did a lknd lead test with some 1mm singles from the db position with the 6mm disconnected to the stop cock. Singles were nulled out
 
I know its really high and realistically only a 20m run, its a terrace with board at the front and stop cock at the back, gas meter i van do externally but no chance on water
[automerge]1598034761[/automerge]

Yes so I did a lknd lead test with some 1mm singles from the db position with the 6mm disconnected to the stop cock. Singles were nulled out
As tel said get a plumber to put a section of plastic in at the point of entry of the pipe
 
is there a gas pipe anywhere near the water stop cock, or could the water bond be connected elsewhere ( as in as close as practicable to the incomer without demolition)?

another solution would be to get a wet-pants to fit a plastic section close to the stop cock
Unfortunately nothing anywhere near where I could get to. The board is at the front door
 
If bonding is utterly impractical, then what about fitting a 100mA delay RCD incomer instead of the main switch and converting it to a TT system? You would need an earth rod, but that might be more practical then ripping up expensive floors.

Just another idea to be discussed!
 
I find it odd that the incoming water supply isnt plastic..... only come accross half dozen lead ones in 17 years
Loads here in South Wales, Its a mix but seems lots havent been replaced
[automerge]1598037150[/automerge]
I understand why these regs are in place but it does seem stupid when the likely outcome will be the client leaving a wylex wooden backed board in place and no gas bond
 
Does it have supplementary bonding of hot-cold pipes, and water-gas at the boiler?

If so, and you bonded to the gas supply, would you then see a very low resistance (of the order of the magic 0.05 ohms) from gas bond to water stopcock?
[automerge]1598037758[/automerge]
The 0.29 ohms you are seeing might be from the boiler's CPC, or gas hob ignition CPC, etc.
 
Does it have supplementary bonding of hot-cold pipes, and water-gas at the boiler?

If so, and you bonded to the gas supply, would you then see a very low resistance (of the order of the magic 0.05 ohms) from gas bond to water stopcock?
[automerge]1598037758[/automerge]
The 0.29 ohms you are seeing might be from the boiler's CPC, or gas hob ignition CPC, etc.
Clever thinking, but are you saying this would then be OK?
 
I find it odd that the incoming water supply isn't plastic..... only come across half dozen lead ones in 17 years


Lots of 22mm, 3/4" and 1" copper or galv' supplies. Lead supply pipes were stopped in 1970 and copper or galvanised steel ones used. Early 70's meant mixed imperial and metric. These were superseded by the black plastic ones mid 70's early 80's (often still found used for "ducting" to outbuildings).The MDPE pipe was available form the late 50's but never took off then. The newer blue one should have either a tracing strip built in or wire inserted so they are easier to find with a CAT and genny. Unforunatly the majority of the ones installed before 2000 don't have this!
 