Discuss Max water bond resistance in the UK Electrical Forum area at ElectriciansForums.net
I know its really high and realistically only a 20m run, its a terrace with board at the front and stop cock at the back, gas meter i van do externally but no chance on water
Out and up the front wall to the eaves, in through the loft, then back out and down the back wall? Assuming loft hasn't been converted.
I like telectrix and Baddegg's idea best
I find it odd that the incoming water supply isnt plastic..... only come accross half dozen lead ones in 17 years
Loads here in South Wales, Its a mix but seems lots havent been replaced
[automerge]1598037150[/automerge]
I understand why these regs are in place but it does seem stupid when the likely outcome will be the client leaving a wylex wooden backed board in place and no gas bond
Does it have supplementary bonding of hot-cold pipes, and water-gas at the boiler?
If so, and you bonded to the gas supply, would you then see a very low resistance (of the order of the magic 0.05 ohms) from gas bond to water stopcock?
[automerge]1598037758[/automerge]
The 0.29 ohms you are seeing might be from the boiler's CPC, or gas hob ignition CPC, etc.
Clever thinking, but are you saying this would then be OK?
I find it odd that the incoming water supply isn't plastic..... only come across half dozen lead ones in 17 years
Lots of 22mm, 3/4" and 1" copper or galv' supplies. Lead supply pipes were stopped in 1970 and copper or galvanised steel ones used. Early 70's meant mixed imperial and metric. These were superseded by the black plastic ones mid 70's early 80's (often still found used for "ducting" to outbuildings).The MDPE pipe was available form the late 50's but never took off then. The newer blue one should have either a tracing strip built in or wire inserted so they are easier to find with a CAT and genny. Unforunatly the majority of the ones installed before 2000 don't have this!
Is it done the way the regs say? No
Is it achieving the goals of the regs? Yes
When comparing the do-nothing option of leaving the old Wylex rewirable CU in place with no bonding, with a replacement RCD/RCBO-based CU and a bonding-by-pipework option, I would have say it is a massive improvement in safety.
Likewise I have only come across a handful of lead water mains still in service. But I have come across plenty of iron/steel ones.
[automerge]1598132114[/automerge]
I may have missed it, but I don't see anywhere where the OP has told us what the earthing system is yet, and nobody appears to have asked.
If it is TT or TNCS then it likely is OK with a 6mm main bond.
System is tncs and it is copper coming out of a floor board at the rear of the house. I could go ripping these up but wasn't going that far on a quote for obvious reasons. Could be anything coming in, I can't see, jouse is victorian
[automerge]1598171927[/automerge]
This is my thinking, its one of those situations where it'll probably all get left an old mess
That is why I would probably see if good gas supply bond & supplementary bonding of hot/cold/gas pipes where accessible is enough to measure the water pipe as well-bonded. It might not follow the specific guidance to the letter, but it does the necessary job.
After all, if you did an inspection and found no sign of water bonding but it measured 0.05 ohms to the MET, how would it be coded? C3 at most. From the best practice guide:
C2 for: Absence of effective main protective bonding of extraneous-conductive-parts entering the premises
C3 for: Main protective bonding to gas, water or other installation pipe is inaccessible for inspection, testing and maintenance, or connection not made before any branch pipework.
My emphasis on the "effective" aspect. Not doing the upgrade to an RCD/RCBO board in my mind is far more dangerous than leaving as-is, so insisting on by-the-regs water bonding that the customer will reject would be a case of perfection as the enemy of good.
Reply to Max water bond resistance in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, has anyone got any experience of resistances through press fit plumbing fittings? Just been to a job I did last year which was a...
Hi guys, sorry if this has been asked before. I’m currently in a flat where the tenant queried the water bonding. There’s a 6mm green and yellow...
Hi guys Does the earth Bonding HAVE to be done at the meter or can it be put on the gas inlet to the boiler in a utility room? Plans have changed...
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
6K