Discuss Max water bond resistance in the UK Electrical Forum area at ElectriciansForums.net

Ampo

-
Reaction score
15
Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and newly decorated walls, coving and so on) and the mains water is opposite side of the house. Although the strap isn't visible I have run a wander lead and got 0.29 on a 6mm at the dB to the stop cock so it is bonded. I know its not a good reading but wonder what peoples opinions are in changing the board? There is no way they want the work done if it involves ripping the house apart for the water bond but they are more than happy to do the board and gas.
 
Hi all so I have a situation where a client is moving and they want the db changed for selling. Db change is easy enough as is running a bond to gas which is currently missing. The only issue is that the last eicr said that the water wasn't bonded. It would involve major works (tiled floors and newly decorated walls, coving and so on) and the mains water is opposite side of the house. Although the strap isn't visible I have run a wander lead and got 0.29 on a 6mm at the dB to the stop cock so it is bonded. I know its not a good reading but wonder what peoples opinions are in changing the board? There is no way they want the work done if it involves ripping the house apart for the water bond but they are more than happy to do the board and gas.
.29 ohms = 94m of 6mm cable, or more likely a loose connection. Could you not run the bond around the exterior of the building?
 
is there a gas pipe anywhere near the water stop cock, or could the water bond be connected elsewhere ( as in as close as practicable to the incomer without demolition)?

another solution would be to get a wet-pants to fit a plastic section close to the stop cock
 
.29 ohms = 94m of 6mm cable, or more likely a loose connection. Could you not run the bond around the exterior of the building?
I know its really high and realistically only a 20m run, its a terrace with board at the front and stop cock at the back, gas meter i van do externally but no chance on water
[automerge]1598034761[/automerge]
could you elaborate on how you tested this please? was this tested with the 6mm disconnected from the MET?
Yes so I did a lknd lead test with some 1mm singles from the db position with the 6mm disconnected to the stop cock. Singles were nulled out
 
I know its really high and realistically only a 20m run, its a terrace with board at the front and stop cock at the back, gas meter i van do externally but no chance on water
[automerge]1598034761[/automerge]

Yes so I did a lknd lead test with some 1mm singles from the db position with the 6mm disconnected to the stop cock. Singles were nulled out
As tel said get a plumber to put a section of plastic in at the point of entry of the pipe
 
is there a gas pipe anywhere near the water stop cock, or could the water bond be connected elsewhere ( as in as close as practicable to the incomer without demolition)?

another solution would be to get a wet-pants to fit a plastic section close to the stop cock
Unfortunately nothing anywhere near where I could get to. The board is at the front door
 
If bonding is utterly impractical, then what about fitting a 100mA delay RCD incomer instead of the main switch and converting it to a TT system? You would need an earth rod, but that might be more practical then ripping up expensive floors.

Just another idea to be discussed!
 

Reply to Max water bond resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, has anyone got any experience of resistances through press fit plumbing fittings? Just been to a job I did last year which was a...
Replies
8
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
915
Hi guys, sorry if this has been asked before. I’m currently in a flat where the tenant queried the water bonding. There’s a 6mm green and yellow...
Replies
4
Views
2K
Hi guys Does the earth Bonding HAVE to be done at the meter or can it be put on the gas inlet to the boiler in a utility room? Plans have changed...
Replies
4
Views
2K
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
Replies
20
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock