Hi guys

Does the earth Bonding HAVE to be done at the meter or can it be put on the gas inlet to the boiler in a utility room? Plans have changed and cables already run ?

Also am I right in thinking that if water inlet is in blue pvc pipe Bonding isn't required even tho it is copper on outgoing side of stop cock?

Thanks
 
Last edited by a moderator:
gas bond should be as close as practicable to within 600mm from where it enters the building and before any joints. if pipe is direct from meter to boiler, then no problem. as for the water, test the copper in case it's extraneous. >22k resistance to MET no bonding required.
 
gas bond should be as close as practicable to within 600mm from where it enters the building and before any joints. if pipe is direct from meter to boiler, then no problem. as for the water, test the copper in case it's extraneous. >22k resistance to MET no bonding required.
I'd say it's definately over 600mm
Looks like I'm gonna have to clip it around the outside of the house
 
regs say a close as practicable. to avoid pikey bait on the outside, near boiler is as close as pracicable.
 

Reply to Bonding gas and water in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing an EICR on a commercial install, there’s a copper pipe comes down a pipe chase with the stop cock fitted onto it, it’s then pvc pipes that...
Replies
2
Views
289
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock