Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
 
You'll have to check with the manufacturer to be sure but I would expect it to be the same as for an MCB with equivalent tripping characteristic.
 
  • Like
  • Agree
Reactions: pc1966 and DPG
Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
It would still be to the type B, C, D trip data. Is it a combined RCBO/AFDD unit? It should be the Zs values given for 61009.
 
  • Like
Reactions: pc1966
It is a combined RCBO/AFDD so would make sense its rated the same. One of the reasons I was asking is that it didn't auto fill when filling out my test sheet so was second guessing. Ill check with the manufacture and will let people know.

Thanks
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex

Thread Information

Title
Max Zs value for AFDD
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Gaz92552,
Last reply from
Gaz92552,
Replies
4
Views
8,214

Advert