Does anyone know where I can find the maximum Zs values for AFDD's? Table 41.3 refers to 60898 and 61009-1 but AFDD's are BS 62606
You'll have to check with the manufacturer to be sure but I would expect it to be the same as for an MCB with equivalent tripping characteristic.
  • Agree
Reactions: pc1966 and DPG
It would still be to the type B, C, D trip data. Is it a combined RCBO/AFDD unit? It should be the Zs values given for 61009.
Reactions: pc1966
It is a combined RCBO/AFDD so would make sense its rated the same. One of the reasons I was asking is that it didn't auto fill when filling out my test sheet so was second guessing. Ill check with the manufacture and will let people know.
Thanks
Reactions: pc1966
Essex
Max Zs value for AFDD
Gaz92552,
Gaz92552,