I like the 35 way. I've always done it this way but its longer . b type 5 times, c type 10 times, d type 20 times. so if its a c type 32amp it would be 230 divided by 320=0.71. 0.71x 80%= 0.56. 0.56 x 0.95 c mim =0.55, long winded so in future might youse the magic 35.
What bothers me about "quick calculations" like 35/In is they end up being used and not understood. Yes, that works fine for a B-curve MCB but not for other cases!
So Farmelectrics method is better as it shows the key point - the 0.4s disconnection is achieved by ensuring the magnetic trip is reached under worst-case conditions (0.95 supply volts and 0.8 for cable temperature on R1+R2).
Can't say I'm a huge fan of this guy, seems a bit harsh after posting his video but I get the impression he doesn't know why it's 35 - also on his site he uses little r1 for a reading on a Radial and few other things ;) that a tutor should know better.
Reply to Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Hi all, I have an assessment exam question that asks for the design value for a 32A 60898 MCB max Zs. By 'design' value is this the regs tabulated...