I like the 35 way. I've always done it this way but its longer . b type 5 times, c type 10 times, d type 20 times. so if its a c type 32amp it would be 230 divided by 320=0.71. 0.71x 80%= 0.56. 0.56 x 0.95 c mim =0.55, long winded so in future might youse the magic 35.
 
What bothers me about "quick calculations" like 35/In is they end up being used and not understood. Yes, that works fine for a B-curve MCB but not for other cases!

So Farmelectrics method is better as it shows the key point - the 0.4s disconnection is achieved by ensuring the magnetic trip is reached under worst-case conditions (0.95 supply volts and 0.8 for cable temperature on R1+R2).
 
Can't say I'm a huge fan of this guy, seems a bit harsh after posting his video but I get the impression he doesn't know why it's 35 - also on his site he uses little r1 for a reading on a Radial and few other things ;) that a tutor should know better.
 

Reply to Max zs values in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
935
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, I have an assessment exam question that asks for the design value for a 32A 60898 MCB max Zs. By 'design' value is this the regs tabulated...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock