Hi All, im new to the forum, ive often browsed various threads with great interest...
I know there's been a fair bit said on this subject so sorry for bringing it up again,
im in the process of a timber frame new build ( 2 bed, 1 study/poss bed 3 )
When working out the maximum demand as p96/7 in the OSG its putting me
over 100a, we all know its never going to get close to that so what what can
i do about it ???
circuits are
2 x 6A lts
1 x 6A smokes
3 x 32A rings ( up/dwn/kit )
1 x 32A hob ( 6.6 Kw ) no gas in the village
1 x 32A oven ( 4.4 Kw ) '' '' ''
1 X 16A for imm ( only 13A )
1 x Air source oil heating system elec supply unknown
so not including the air source heating & the smokes im getting 112.82 Amps,
how can i get around this, all views are welcome....