Don't recall the post quoted above, but that will be split concentric cable. The insulation on the individual neutrals in this cable is thin and fragile, making it more susceptible to neutral - earth faults than other cables.

Interesting, is it a particular brand of cable that you've had this problem with?
 
Interesting, is it a particular brand of cable that you've had this problem with?
No particular brand. It's a characteristic of the cable - the insulation on the neutrals is thin and easily damaged, especially inside the CU.
I normally twist the neutrals tightly together and wrap the bunch with a few layers of PVC tape.
 