MCCB vs HRC overcurrent protection

Discuss MCCB vs HRC overcurrent protection in the Electricians' Talk | All Countries area at ElectriciansForums.net

B

baldsparkies

Have been looking at a situation where a 400 amp MCCB is feeding a ups. There is a mains supply to a genny changeover switch, along with the genny supply, and the MCCB is between the genny switch and the UPS.
Yes its a big bu##er.

Any ways there was a momentary power fluctuation which threw the mccb, great because the change over would not have seen this, cus the main supply would still be on to it.
That meant the genny didnt kick in and walla a problem once the ups powered down.

Now my question, MCCB's are notorius as we know for kicking out when hit by surge current as probably happened here. All we needed to do was to re set the thing. but of course the damage is done by then.

What do you clever types think about replacing the MCCB with a 400 amp switchfuse with HRC links instead of the MCCB. Before you ask, the thing is dialled up to max, Load test shows 280 amps running full load.

I reckon its the best way forward but wanted to pick yer brains
The install is top notch. All composite panels, monitor equipment PFC installed, should be a dream if not for this one week link in the chain.

UPS supplys are all individual 150mm tri rated cables, so nice and bendy to work with.

Thanks for your input in advance. ;)
 
AS said MR E, if not for this one weak link.
Change over switch just aint going to see a loss of power on the load side, only the supply.
And even if the genny did kick in, the mccb is still out so the supply would stop at that point,

Anyway I digress, Can HRC's cope with surge better than those blooming MCCB's ????? I reckon yes but your thoughts appreciated.

By the way, I have never seen a supply change from mains to genny in milli seconds, Thats where the ups comes in handy, gives enough time for the genny to fire up.
 
Last edited by a moderator:
I would think about your proposal to replace an MCCB with a Switch-fuse.
Switch-fuses have there own inherent disadvantages, one important aspect is ''phasing'' where one of the 3 fuses blows... They are also expensive to incorporate any control mechanisms!!

Why do you say a 400A MCCB is wound up to it's highest setting, when the full load has been measured at just 280A?? Are you sure this is a 400A breaker or is the 400A just the frame size?? Can you tell us the manufacturer of these MCCBs?? One other question, ...Are these MCCBs, Changeover Switches, etc, mounted in a common Switchboard panel??
 
My guess is the setting has been adjusted up to max because the same problem occured 18 months ago. They get a blip in the mains, not an outage, and its tripping the mccb.
I have been to office blocks and factories over the years were there has been power failures. When the power reinstates, some but not all of the mccb,s trip out. I put it down to the loads they supply are coming on line in one hit. I do take your point on phasing, but the equipment supplied is all single phase. Really I am just wondering if HRC's are less prone to blowing than mccb,s to tripping. As an example the DNO cutouts always have HRC's. When power fails its rare for these to blow when the supply comes back in. Oh yes almost forgot its a 400A mccb for sure calibrated from 160 to 400 amps.
I need to get more detail cus this all occured at 2.30 in the morning, so not at my best. There must be an answer to the problem somewhere.
 
Last edited by a moderator:
HRC fuses are used by the DNO because fuses present the cheapest method of providing PSCC protection to an installation...

From what you describe, as in the ''Blips'', This can easily be protected against by provision of Surge Protection.

I don't know of any manufacturer of MCCBs that have a setting range on a 400A breaker of 160A to 400A!! I think that your 400A is a frame size, and that the actual size of this breaker is in the region of around 280A to 300A, depending on manufacturer.

Are you saying that this breaker (MCCB) is single phase, or just that the final loads are single phase?? If it is the latter, the UPS isolation transformer along with many other components in the UPS will be 3 phase and will not like at all, a situation where it's supply is single phasing!!!

If you can give a little more information, after you have been back and assessed the situation on this installation it would be helpful, and a pic or two even more so....
 
Last edited by a moderator:
Many thanks 54, Will check the frame size,
You are probably correct in that the 160 to 400 is reffering to this rather than the calibration of the device.
The information received is second hand, over the phone regarding details.
We re set the mccb with no problems. They can offer a fair bit of resistance before latching in as you will know.
The loadings were around 280 per phase fairly well balanced but it IS a 3 phase supply feeding single phase loads on the load side of the ups.
We need to isolate and remove the cover, because apart from what was readily visible, and conducting a load test whilst there, The rest of the info was coming from the O&M manuals, which they found the following morning.
We are going back up during the day, so will get a better assesment of the situ then.
Many Thanks for your input.
PS. Point well taken regarding single phasing, not a road to go down.
 
Last edited by a moderator:
Can you adjust the time lag coefficient on the MCCB? A small mains blip shouldn’t cause nuisance tripping.
What’s it going out on over current or under voltage? I had a problem with U/V on an ACB a few years ago, 2ms delay solved the problem.
 
Can you adjust the time lag coefficient on the MCCB? A small mains blip shouldn’t cause nuisance tripping.
What’s it going out on over current or under voltage? I had a problem with U/V on an ACB a few years ago, 2ms delay solved the problem.

Many thanks Tony,

I will have a look at the calibration settings when on site and take it from there.
Some units have 2 dials covering trip threshold marked In and Io, others are even more flexible with 3 dials, the third covering Isd which I believe is the prospective fault current.
i usually multiply the nominal rating set on dial 1 Ir by the Io and Ir calibrations.
Any other info would be much appreciated, but my guess is they have been gradually increasing loadings, and as a result a loss of power, even though momentary would mean a sudden surge through the device which would re instate under full load is causing the tripping. So hopefully re calibration could well be the answer. They also need regular checks on the system to ensure max demand criteria remains within the design parameters of the install, but you would think that would be common sense.
 
That old chestnut again, has anything changed? No! Well, we added this and that and oh, that other bit, but nothings changed! (Well it’s only bits of stuff).

A different scenario but I had to up rate an ACB from 800A to 1200A and add a 3rd feeder cable etc. But nothing had changed! Someone sneaked the 300HP compressor in under the cover of darkness!
 
Aint that the truth Tony, Often with the bigger companies, they have various contractors adding here and adding there with no one keeping check on who's doing what, where and why. I remember on one site Red phase had 80 amps Yellow 260 and Blue 140. But it happens all the time, at least on this one the phases are pretty well balanced so no issues there. Thanks for the responses to all.
 

Reply to MCCB vs HRC overcurrent protection in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock