The manual is very basic. There is a diagram, that's about as much info as you get.
View attachment 32230
Gaz your getting Zs & Ze confused mate. (going by the picture you posted up)
The MI3000 on screen display shows you how many probes to use and which probes to use on every test you perform. Select any test function and have a look at the bottom right hand side of the display screen. Three circles L, N & PE. If the circle is solid/black then you need to attach a probe to that test lead. eg:-
Zs = a 3 probe test. Pre-select the type of MCB (eg bs60898 32A), plug in using an adapter (safer than using probes btw) and it will give you a reading and work out if it is acceptable to AMD3 Regs for you.
Ze = a 2 probe test taken at the DB with the probes on Line and Earth. Have a look at the bottom right display screen before any test just to make sure you have set it up correctly.
When carrying out a Zs and the MFT prevents you from doing so, a X will appear. This is due to earth leakage from energized circuits whilst trying to test. With permission (etc, etc, etc) turn off the main switch and conduct the Ze test. Now find out where the leakage is coming from lol.
The lads at Test Meter can answer this question a lot better than most of us on here regarding your Metral, send them a PM and I'm sure they will be happy to help.