S slacky1230 ~ Jul 29, 2017 #17 although it's a solution to bypass and test on hi current I'd rather get my meter sorted so it's working correctly.
although it's a solution to bypass and test on hi current I'd rather get my meter sorted so it's working correctly.
T The Ghost Jul 30, 2017 #18 Yeh but is it working incorrectly. It does happen noise. Is this domestic or commercial. I have not encountered noise in a domestic so far but a couple of times in commercial offices.
Yeh but is it working incorrectly. It does happen noise. Is this domestic or commercial. I have not encountered noise in a domestic so far but a couple of times in commercial offices.
S slacky1230 ~ Jul 30, 2017 #19 I know it can happen now and again but it's near enough all the time. I've tried it in 3 commercial places with the same result.
I know it can happen now and again but it's near enough all the time. I've tried it in 3 commercial places with the same result.
T Toneyz Jul 30, 2017 #20 All I can note I have only had the same experience as Vortigern only a few times at commercial places on my Megger MFT.
All I can note I have only had the same experience as Vortigern only a few times at commercial places on my Megger MFT.
S Strima Jul 30, 2017 #21 I've seen it a lot on Flukes, mainly telecoms sites and working on generators. Megger has always seemed to take noisy earth in its stride.
I've seen it a lot on Flukes, mainly telecoms sites and working on generators. Megger has always seemed to take noisy earth in its stride.