When I had separates, the Megger LTW325 I had was rather hit and miss on the low current tests. I sometimes used to use the trick mentioned in the Kitcher book - lock off breaker / RCBO, join L and CPC at circuit end, and use a high current test between bus bar and outgoing live at CU. It had the extra benefit of thoroughly confusing anyone watching too!
and elimunates any false readings caused by RCD. must remember to remove the short brfore energising though.
 