Sep 3, 2025
1
0
50,001
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
IMG_1914.jpegI have a Memera 2000 ad fuse box. 5 yrs ago it passed the Landlords electrical certificate but now I’ve been told it has failed. The reasons are: the bathroom light is a pendant and the other reason is that the light is connected to the left side of the circuit box and it needs to be connected on the right. I understand the light fitment did need changing and so I’ve now fitted a new IP65 light fitment. Have the regs changed over the past 5 years and does the bathroom light now have to be wired into a seperate fuse on the right side as I thought this was an advisory not a fail.
 
Did they also point out the non compatible mcb and blank plates.
 
  • Like
Reactions: PS Electrics
View attachment 123325I have a Memera 2000 ad fuse box. 5 yrs ago it passed the Landlords electrical certificate but now I’ve been told it has failed. The reasons are: the bathroom light is a pendant and the other reason is that the light is connected to the left side of the circuit box and it needs to be connected on the right. I understand the light fitment did need changing and so I’ve now fitted a new IP65 light fitment. Have the regs changed over the past 5 years and does the bathroom light now have to be wired into a seperate fuse on the right side as I thought this was an advisory not a fail.
Depends

Is there sufficient supplementary bonding in the Bathroom?

If you move the Lighting MCB over then all power will be lost in the event of the RCD tripping which isn't ideal. Also the Smoke Detector is on that circuit and you don't want that losing power with an earth neutral fault on any circuit. It looks like the downstairs lighting was moved over at some point and the labelling was not updated.

There is also the points Westward made.
 
IMG_0717.png
 
So the parts above sort the issues highlighted, you just need to sort some suitable blanks.IMG_0718.pngi think this is the right one and you will need 3 of them.
 
Last edited:
Cheaper to get a whole new board than those add-on pods….. and it’ll come with an SPD and be metallic.


The thing with EICRs is that it is totally up to the engineer doing the report as to how strict or lenient they want to be.
You could have a slew of C3 notes, which would bring a satisfactory outcome, but if one of those is raised to a C2….. which means “potentially dangerous” situation, would make it unsatisfactory…. And “fail” the report.
 
Cheaper to get a whole new board than those add-on pods….. and it’ll come with an SPD and be metallic.


The thing with EICRs is that it is totally up to the engineer doing the report as to how strict or lenient they want to be.
You could have a slew of C3 notes, which would bring a satisfactory outcome, but if one of those is raised to a C2….. which means “potentially dangerous” situation, would make it unsatisfactory…. And “fail” the report.

I have to agree can't see the sense in spending that much on this board.

So many benefits of a new board compared to the configuration of this one, it is what I would go for.
 
  • Like
Reactions: DPG
I could be wrong but I'm pretty sure they never produced blank plates for Memera 2000 or Memshield 2.
 
The existing blanks are MEM. I've used 100's of them.

The issue though is that they look like they are removable without a key or tool and the lid isn't lockable so it is a C2.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Memera 2000 ad fuse box. Passed Landlords electrical test 5yrs ago but has now failed. Why?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Getting Their,
Last reply from
brianmoooore,
Replies
11
Views
220

Advert