zedess

-
Reaction score
22
Going to do a consumer unit change and earthing upgrade on tt system for my coming assessment in two weeks,straight forward enough.. all earthing straight to the consumer unit..untill i look in the IEE ELECTRICIANS GUIDE TO THE BUILDING REGS..which shows a main earthing terminal, and 16mm to the consumer unit ( as per TN systems) which way would u go for an assessment ? does it make any difference? thanx
 
Staight from the earth spike to the consumer unit is always best. Less liklyhood of any of the protective earths being disconnected in the CU.
 
As long as it can be easily disconnected for testing then external MET (labelled correctly) or CU is fine. Many people go for external MET as it can be awkward to get out of the CU block, but personally, I prefer keeping it all in the CU.
 
yeah either way is fine. External or within your CU both terminals are officially METs, all you are doing is extending the capacity of the MET by adding the external one, dont forget for the external one you should have a warning on or near saying " safety electrical connection - do not remove"
 
My preferred installation is always to an external MET. Everything accessible without having to start taking CU/DB covers off and fighting your way through dressed cables to disconnect earthing and bonding cables for testing!! lol!!
 
My preferred installation is always to an external MET. Everything accessible without having to start taking CU/DB covers off and fighting your way through dressed cables to disconnect earthing and bonding cables for testing!! lol!!

Totally understand where you are coming from with this, and with some CU's which are very awkward, I go external. I generally install Crabtree starbreaker units and find it quite easy to get to the MET inside.
Each to their own tho :)
 

Reply to MET on a TT system? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock