I have a customer who is the Building Manager of a commercial office building. There are 17 sub-let office areas, each with their own 3-phase meter. There is apparently a suspicion that some of the meters are not accurate and we've been asked to validate the readings on all 17. Not had a job of this nature before, and following some brief research it seems there are 2 practical options: wire in an additional, temporary calibrated meter, or measure using a power quality analyser or equivalent meter.
The meter option would not require anything to be disconnected as it can be clamped around the incoming supply.
The supply to each sub-let area can be isolated from the basement if the additional meter option is used.
Has anyone done this before? If so, what method would you recommend and how long should the meter be monitored for in order to get an accurate reading (i guess a min of 48 hours weekdays)?
Any advice would be much appreciated.
 
I would fit a calibrated check meter. But as for how long? this depends on the usage of the units.
 
I think you're going to need more than one temporary calibrated meter, if you have 17 meters to check!! lol!! You'll realistically need at least a 48 hr measuring period, that covers 2 working days to compare. Vary rare for meters not to be accurate or develop measurement faults, not unheard of mind, just very rare!! lol!!

Have you checked that each of these meters installations are not supplying hidden illegal hook-ups to elsewhere??
 