Guys, how do I work out what to set the overload for in a DOL starter? the motor says 1.1kw on the top of it.
240 or 230?OK, so flc will be approx. (1100/240) /0.8 i.e. 5.73A, so select an overload 5A -7A, and set at 6A. then clamp it while running to fine tune.
how would you do this in practice? if the motor was a complete new install I would need to choose the overload before the motor was connected. I couldn't then clamp it until afterwards. chicken and egg type thingyIf possible clamp the existing set-up beforehand as this formula Tel has used is good for your basic bog standard motor by if you motor is non-standard or specialised then it may have different running characteristics and its to be assumed when clamping that the motor is working within its design parameters i.e. its not overworking due to blockage or bearing wear etc etc...